So that you will have 40 amps of service capable of 120 / 240 volts.40 double? lost me there.
I would agree with this. With mine I had to start from scratch (all it had was a 14ga 120v circuit running out to it). I plan on running a 1/0 underground service and having the garage have it's own panel. In my situation it just works better for me due to the distance my garage is from my house. Your setup ie: house/garage spatial relationship is going to dictate a lot of what you can do or to what extreme you want to go. I know some guys will disagree, but I think a garage that doesn't have 220v to at least one point is a mistake. If you are going to the work, do it so you won't have to upgrade later or if you sell someone won't have to redo your work. Just my opinion.So that you will have 40 amps of service capable of 120 / 240 volts.
As to your original question I don't think that the 30 amps of 120 is near enough! I am a staking engineer and recommend no less than 60 amps for most garages running minimal equipment and lights.
If you are the only one using ANY power equipment at one time you can get by on 30 amps, but you are pushing it.
Also, how far is the garage from the meter base location? You must consider the voltage drop due to distance in relation to your wire size. You never want to fall below 105 volts or you will burn up your equipment. Most problems with "garage" wiring is related to voltage and not amps.
Also,yeah my plan is to run it through pvc pipe underground to my garage to keep it semi protected. i understand that this is a temporary thing until i can do a serious upgrade to the garage.
4 recepticles and 4 switches does not make 8 circuits.it depends on how much stuff you want out there you can have 8 circuits on 1 breaker ( say 4 outlets and 4 lights equal 8 circuits) if you plan on running alot of power tools i would put a 50 amp double pole breaker and run 8 guage wire to your garage and put in a sub panel
Good advice here, but if the sub panel is in a separate building you need to drive a separate ground rod at the separate building. Article 250 NEC. Technically it's what is called a separately derived system and the ground from the existing panel is not necessary, but certainly won't hurt anything. The important thing is the separate ground rod is required at a separate building.4 recepticles and 4 switches does not make 8 circuits.
1 breaker = 1circuit.
Your best option is to install a subpanel in your garage. The size of the circuit feeding the panel depends on your expected loads. If you are just going to be using small hand held tools and lighting you can get away with a 30 amp circuit. If you are going to be running compressors, table saws or other large equipment you should have a 40 or 50 amp feed.
You can get a 4, 6, or 8 space panel. The panel can be rated for any current greater than the rating of the feeder circuit. In order to properly feed the panel you will need to run a 4-conductor cable [2 hots(red and black), 1 neutral(white) and 1 ground(green or bare copper)]
In the main panel: you will connect the hot wires to a 2 pole breaker, the neutral and ground will attach to the grounded bus(just like all the other cicuits in the panel.
In the new subpanel: you will attach the hot wires either to the main breaker (if the panel is equiped with one) or to the main lugs. The neutral wire will attach to the aluminum bus similar to the bus in the main panel. {Important note: DO NOT INSTALL THE GREEN BONDING SCREW THAT GROUNDS THIS BUS TO THE PANEL} The neutral wire is only to be grounded at the primary panel. You will need to install a separate ground bar directly to the panel box and attach the ground wire to it.
When installing new circuits in the subpanel the white wires attach to the neutral bus and the ground wires attach to the ground bar.
If you have any questions, or need anything clarified drop me a PM. If necessary I'll give you my phone # if you need to discuss anything further.
Larry
FYI - I have over 25 years experience as an electrician